General Category => General Discussion => Topic started by: calisto on September 09, 2021, 09:55:07 AM
-
I am retrofitting my Bridgeport mill. I have chosen Mach 4, PMDX 424 and StepperOnline 12N-m closed loop stepper motors for the conversion. I am having trouble with my x axis faulting out and I would like for the system to shut down if one of my drives faults out. I currently do no have the ALM+ and ALM- (from the drives) wired into my SmartBOB because I am uncertain how to go about doing it. Can I simply wire these in series with my E-Stop (pin 27 and 28). Please advise
-
You should be able to connect all of the ALM- wires together and connect them to the PMDX-424's "COM" terminal on the EStop connector (J14). Then tie all the ALM+ wires together and connect them to the PMDX-424's FAULT terminal on J14. The PMDX-424 provides a pull-up on the FAULT terminal. As best I can tell from the StepperOnline Y series closed loop stepper driver manual, a fault condition will turn on the driver's opto-coupler, thus shorting ALM+ to ALM-, which will then connect the PMDX-424's FAULT input to COM, which will disable the PMDX-424 same as an EStop. And the FAULT going active gets reported to Mach4 same as an EStop.
-
Thank you. I will try that out